High Voltage Current Transformer CT Comprehensive Tester
Introduction:
High Voltage Current Transformer CT Comprehensive Tester is a fully automated PT, CT characteristics tester, and among the tests this equipment can do
includes
CT/PT Volt-ampere characteristics test,
CT/PT Polarity test, CT/PT Variable test, CT/PT T
urns ratio test,
CT/PT
Ratio error and phase angle error test,
CT/PT
Winding resistance measurement,
CT/PT
Secondary loop burden measurement, CT Excitation curve and parameters test, CT nameplate guess and Error line curve test for protection CT
Features:
• There is no need to attach any additional equipment; the testing topic will complete itself.
• Result printing is simple with the built-in printer.
• LCD monitor with a large screen and graphics.
• Excitation knee point value, 5% and 10% error curves are automatically displayed.
• Save 1000 groups data.
• With USB port. The data can be saved in USB disk and read by PC(WORD format file).
• Portable design about 35kg, suitable for on-site test.
• Engineering plastic box with damping, strong and reliable.
Specifications:
| Test standards | IEC60044-1, IEC60044-6, GB1208, GB16847, C57.13 |
| Power supply | AC220V±10%,50Hz/60Hz±10% |
| Power output | 0.1~125V (AC) |
| Current output | 0.001~5A(RMS) |
| Power output | 300VA |
| Maximum knee voltage measurement | 45kv |
| Current measurement | Range: 0~10A (automatically change range in 0.1/0.4/2/10A) |
| Error: <±0.1%+0.01%FS | |
| Voltage measurement | Range:0~200 V (automatically change range in 1V/10V/70V/200V) |
| Error: <±0.1%+0.01%FS | |
| Turns ratio measurement | Range: 1~30000 |
| 1~1000 error<0.05% 1000~2000 error<0.1% 2000~30000 error<0.2% | |
| Phase measurement | error: ±2min resolution: 0.01min |
| Coil resistance measurement | Range: 0~8kΩ (automatically change range in 2ohm/20ohm/80ohm/800ohm/8kohm) |
| Error: < 0.1%RDG+0.01%FS | |
| Maximum resolution: 0.1mΩ | |
| Temperature measurement | -50~100 Celsius degree, error<3 Celsius degree |
| CT Secondary burden | Range: 0~160ohm (automatically change range in 2ohm/20ohm/80ohm/160ohm) |
| Error: <0.2%RDG+0.02%FS | |
| Maximum resolution: 0.001ohm | |
| PT Secondary burden | Range: 0~80kohm (automatically change range in 800ohm/8kohm/80kohm) |
| Error: <0.2%RDG+0.02%FS | |
| Maximum resolution: 0.1ohm | |
| Saved data groups | >1000groups |
| Work condition | Temperature: -10ºC~50ºC moist: ≤90% |
| Size | 485mm×356mm×183mm |
| Weight | <15Kg |