High Accuracy Transformer Current & Voltage Testing Device
Characteristics
The CT PT Analyzer is extensively utilized in the installation, testing, and maintenance of transformers in power transmission and distribution systems, power plants, and related industries. It can perform various functions, such as testing turn ratio, phase angle analysis, excitation current measurement, polarity check, burden measurement, coil resistance testing, short-circuit impedance measurement, and saturation analysis.
Testing and resultsTest standard |
IEC60044-1/2/5/6
IEEE C57.13 |
I nput power voltage | AC220V±10%,50Hz/60Hz±10% |
Output voltage and current |
0.1-180V(AC)
0.001-5A(RMS) |
Output power | 500VA |
Max. inflection voltage | 45KV |
Current measurement |
Range:0-10A(Automatic measuring range 0.1/0.4/2/10A)
Error :<±0.1%+0.01%FS |
Voltage measurement |
Range:0~200 V (Automatic measuring range 1/10/70/200V)
Error :< ±0.1%+0.01%FS |
Turns ratio measurement |
Range:1-35000
Error :<0.05% (1-5000) <0.1% (5000-35000) |
R atio measurement |
Typical error <0.02%
Guaranteed error <0.1% |
Angle difference measurement | Accuracy: ±2min, Resolution: 0.01min |
Secondary winding resistance measurement range |
Range:0-8000Ω(Auto range 2/20/80/800/8000Ω)
Error< 0.2%RDG+0.02%FS Maximum resolution: 0.1mΩ |
T emperature measurement |
-50
-
100 degrees
E rror <3 degrees |
CT secondary load measurement |
Range:
0
-
160ohm(2/20/80/160ohm)
Error : 0.2% RDG + 0.02% FS Maximum resolution : 0.001ohm |
PT secondary load measurement |
Range:
0
-
80kohm(800ohm/8kohm/80kohm)
Error : 0.2%RDG+0.02%FS Maximum resolution : 0.1ohm |
PT Turns ratio measurement |
Range: 1
-
30000
Error : <0.1% ( 1 - 10000 ) <0.2% ( 10000 - 30000 ) |
E lectromagnetic PT ratio measurement |
T
ypical error <0.05%
G uaranteed error <0.1% |
Electromagnetic PT angular difference measurement | E rror <3 points |
Number of data storage groups | M ore than 1000 groups |
W orking conditions |
T
emperature: -10 ºC
-
50 ºC
H umidity: ≤ 90% |
Size | 490mm×360mm×190mm |
Weight | 15 Kg |